Right now I have a aux. 90 L tank that I use for my truck. I am wanting to know if there is a way to get it setup with a heater and a fuel level gauge? Thanks guys
Reply With Quote
  #2  
Old 05-03-2011, 01:38 PM
Roboto's Avatar
Roboto Roboto is offline
Gettin Greasy
 
Join Date: Jan 2011
Location: Missouri
Miles on Grease: y=Mx+b
Posts: 1,062
Default

Fuel level sensor is no problem. Need to know the depth of the tank, drill the hole, drill the mounting holes, order the correct length fuel level sender (normally 33 - 240 ohms) and wire it up to a matching gauge

http://www.egauges.com/vdo_send.asp?...uel_Level_Tube

As far as the heat goes, RDS puts a tube in at build time for coolant to pass thru the tank. This is the one you get from Jay. If you already have a tank, you have to find a way to put heat into it. Some folks use a hotfox

http://www.arctic-fox.com/sitepages/pid40.php

But I am working on something similar to this:

http://www.google.com/imgres?imgurl=...KIbKgQf339jpBQ

Scroll down to the in tank heat exchanger

One of the issues that I have with my flat bottom tank with the pickup on the far right is that around 1/2 tank the fuel sloshes away from the pickup around corners, so a sump, or a method to hold oil in place (like the coils in the pic) is helpful to keep your light green.
Reply With Quote
  #3  
Old 05-03-2011, 01:55 PM
skyskijason's Avatar
skyskijason skyskijason is offline
Gettin Greasy
 
Join Date: Aug 2008
Location: N. Georgia
Miles on Grease: 330,000
$ Estimated Saved: at least a little
MacGyver Rating: 1.5
Posts: 4,518
Default

WOW!! That is an EARLY version of the Frybrid in-tank HE!!! Cool pic.

I would shy away from trying to heat the tank the way BFT/RDS tanks are heated. The biggest issue is trying to secure the HE tubing so it does not move around in tank and fail/leak from fatigue. Its gonna be tough to secure properly without adding more access/holes to the existing tank. The same problem exists with DIY knock-offs of the FB HE - the modern version (like, all but 3 like the one linked above) have a sump of sorts built-in around the pick-up which helps with the problems associated with such a big, FLAT tank bottom and also focuses the heat on a small amount of oil instead of the 'whole tank'.

Keep us posted and please attach some pics when ya get done!
__________________
2001 F350 XLT 4x4, dually flatbed. 6637 air filter, single-shot injectors, straight-piped, BTS tunes, 200 gal main VO tank - 180k greasy miles
2000 Excursion Limited 4x4. V3, AIS intake, BTS trans & tunes - 120k VO miles
veggiegarage.com authorized installer

RIP X & Toyhauler - you served us well.
Reply With Quote
  #4  
Old 05-03-2011, 01:59 PM
Clay Clay is offline
Unapologetically American
 
Join Date: Jul 2008
Location: Oklahoma
Miles on Grease: 250,000
$ Estimated Saved: $50,000
MacGyver Rating: 9
Posts: 10,353
Default

Wow, Frybrid has completely changed there ITHE design.
Reply With Quote
  #5  
Old 05-03-2011, 02:25 PM
Roboto's Avatar
Roboto Roboto is offline
Gettin Greasy
 
Join Date: Jan 2011
Location: Missouri
Miles on Grease: y=Mx+b
Posts: 1,062
Default

Let's try this again,

Here is a better pic:

http://www.google.com/imgres?imgurl=...Gs7ogAel9_znBQ

There is a complete unit and a cutaway view.
Reply With Quote
  #6  
Old 05-03-2011, 02:33 PM
Roboto's Avatar
Roboto Roboto is offline
Gettin Greasy
 
Join Date: Jan 2011
Location: Missouri
Miles on Grease: y=Mx+b
Posts: 1,062
Default

Quote:
Originally Posted by skyskijason View Post
WOW!! That is an EARLY version of the Frybrid in-tank HE!!! Cool pic.

I would shy away from trying to heat the tank the way BFT/RDS tanks are heated. The biggest issue is trying to secure the HE tubing so it does not move around in tank and fail/leak from fatigue. Its gonna be tough to secure properly without adding more access/holes to the existing tank. The same problem exists with DIY knock-offs of the FB HE - the modern version (like, all but 3 like the one linked above) have a sump of sorts built-in around the pick-up which helps with the problems associated with such a big, FLAT tank bottom and also focuses the heat on a small amount of oil instead of the 'whole tank'.

Keep us posted and please attach some pics when ya get done!
In a perfect world, I would have done this tank myself. Try to envision an upside down frybrid HE that extends into a sump below the tank. So, you have maybe a 3" sump out of the bottom of the tank, for which you would need to put a hole into the bed of the truck. The benefit would be that you could run all of your hoses under the truck, and you would have a heated sump that eliminates cornering issues while only heating the oil directly around the sump.

It may seem odd to put such a large hole in the bed, but then you wouldn't need to put a hole in the corner, which is almost as large. And if fixes the weakness of the RDS tank.

What I envision is something like the sump here:

http://www.hellmannperformance.com/

with the aluminum coils built into it.

Now that I am doing my new Ex, I probably won't get back to this project until mid summer. I'll let you know what I come up with.
Reply With Quote
  #7  
Old 05-03-2011, 03:49 PM
Mdub707's Avatar
Mdub707 Mdub707 is offline
Me MacGyver!
 
Join Date: Apr 2010
Location: Amsterdam NY
Miles on Grease: 12,000
$ Estimated Saved: $2500
MacGyver Rating: 6.5
Posts: 2,473
Send a message via AIM to Mdub707
Default

Quote:
Originally Posted by Roboto View Post
In a perfect world, I would have done this tank myself. Try to envision an upside down frybrid HE that extends into a sump below the tank. So, you have maybe a 3" sump out of the bottom of the tank, for which you would need to put a hole into the bed of the truck. The benefit would be that you could run all of your hoses under the truck, and you would have a heated sump that eliminates cornering issues while only heating the oil directly around the sump.

It may seem odd to put such a large hole in the bed, but then you wouldn't need to put a hole in the corner, which is almost as large. And if fixes the weakness of the RDS tank.

What I envision is something like the sump here:

http://www.hellmannperformance.com/

with the aluminum coils built into it.

Now that I am doing my new Ex, I probably won't get back to this project until mid summer. I'll let you know what I come up with.
I'm going to be completely redoing my entire tank. I may just start from scratch and sell this one off actually. Instead of cutting a giant hole in the bed for the sump, I'm either going to just raise the bottom of the tank slightly so a sump will fit under and still not have to go through the bed or I may just design a new tank to fit on the frame rail, and give me some bed space back. Either way, a heated sump is going in. I should be getting some form of a heated sump from the same guy who did my filter housing, just need to sit down and hash out some details. I'm excited to get a new tank design on the truck though. I only have one tab on my RDS tank left holding it to the bed, cause they break off.
__________________
2006 F-250 6.0 4x4 SC/SB Greasin since 08/18/2010
SCT Xcal2 w/Innovative Diesel Tuning 466/772 7/19/08
Quote:
Originally Posted by Snake View Post
Cause his job is to make oil and break things.
Reply With Quote
  #8  
Old 05-03-2011, 03:55 PM
Fanderson Fanderson is offline
1997 CC PSD
 
Join Date: Aug 2010
Location: Missoula, MT
Posts: 336
Default

Quote:
Originally Posted by Mdub707 View Post
I only have one tab on my RDS tank left holding it to the bed, cause they break off.
Wow, really? Is this a common problem? Guess I should regularly check mine. Sorry for the thread drift.
Reply With Quote
  #9  
Old 05-03-2011, 04:51 PM
bigwheel bigwheel is offline
Newbie Vegistroker
 
Join Date: Apr 2011
Location: Durango, CO
Posts: 4
Default

Which sump do you guys rec. and do you know of a build thread with pics of this done? Thanks
Reply With Quote
  #10  
Old 05-03-2011, 04:58 PM
Mdub707's Avatar
Mdub707 Mdub707 is offline
Me MacGyver!
 
Join Date: Apr 2010
Location: Amsterdam NY
Miles on Grease: 12,000
$ Estimated Saved: $2500
MacGyver Rating: 6.5
Posts: 2,473
Send a message via AIM to Mdub707
Default

Quote:
Originally Posted by bigwheel View Post
Which sump do you guys rec. and do you know of a build thread with pics of this done? Thanks
If anything is out there it's custom at this point. I'm basically going to copy the Hellmann sump myself, but add ports for coolant to flow through the sump body itself. Roger (Roboto) already posted a link to the sump itself. Not really much to the sump, but adding the coolant jackets should be interesting...

When I get to this step I will definitely post updates. Maybe spark some ideas for other guys.

Quote:
Originally Posted by Fanderson View Post
Wow, really? Is this a common problem? Guess I should regularly check mine. Sorry for the thread drift.
Not sure. I think part of the issue was the supplied hardware. The nuts bottomed out on the threads of the bolt, and were still a touch loose. My guess is it had just enough slop to move around and keep bending those tabs until they broke. The one single tab holding it seems to be doing well. God knows how many boosted launches I've done with only 2 tabs holding it.
__________________
2006 F-250 6.0 4x4 SC/SB Greasin since 08/18/2010
SCT Xcal2 w/Innovative Diesel Tuning 466/772 7/19/08
Quote:
Originally Posted by Snake View Post
Cause his job is to make oil and break things.

Last edited by Mdub707; 05-03-2011 at 05:01 PM.
Reply With Quote
Reply

Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Forum Jump


All times are GMT. The time now is 04:27 AM.


Powered by vBulletin® Version 3.7.2
Copyright ©2000 - 2018, Jelsoft Enterprises Ltd.